On the RUT951 POE+ I configured Wireguard as a client to connect to the Wireguard server at the office. Everything works fine and the WIreguard service is up … until there’s a power failure on the side of the RUT951. IWhen the power is restored, it powers back up and it says/seems the WIreguard is up and running. But there is no connection with the server although in the settings it says the Wireguard is up. (Even if I wait for about 20 minutes or more; Wtachdog interval at 5).
When I then shut down the Wireguard service and save it then restart the service and save again, after about a minute the Wireguard connection is back up and there’s again a link with the server.
The firmware is at 07.19.4 (the latest stable FW).
I have set the Watchdog interval to “5”.
The Persistant keep alive is at “20”.
How can I make sure the Wireguard service is really up and running after a power failure when the power comes back up and the RUT951 has restarted? Is this possibly a bug in the system?