Using two modbus protocols RUT956

Hi all,

I have a RUT956 and would like to connect two Sensors. One sensor having a Modbus TCP/IP connection and another sensor using RS485 RTU protocol. Can both protocols be used at the same time to send the sensor data back to a SCADA system via the RUT956 Router?

Hi Evolv3,

Welcome to Tetlonika Networks Community!

Yes, it is possible for Modbus TCP and Serial Client to be enabled at the same time. Additionally, you can send this collected data via Data to Server feature.

Let me know if this helps.

Regards,