Hello,
Modbus requests and the Modbus SERIAL Client are enabled. The period is 10.
I’m wondering because in the MQTT Explorer there ist an “N/A” from the DataServer (First Line of the ScreenShot) an not an “Empty” from the second line (Modbus Data Input).
The question is whether the DataServer (line 1) gets data from the Modbus definition (line 2). I think, if there are no modbus data, there must be an “empty”.
Hi,
I put some screenshots and a description into a PDF file. This can be done via the following link. Unfortunately, I cannot attach multiple screenshots or files here.
I had already used the Modbus configuration with the old OS on a RUT 955. But because of IPV6 I had to switch to the new OS and a new router.
Sorry for the lon response time.
But I reached my maximum possible posts yesterday.
I can enable the SerialServer OR the Modbus Serial Device Configuration. Not both.
Now, I have disabled the Serial Server and enabled the Modbus Serial Device Configuration.
Thats how it works. I thought the serial server was also required.
Only one service can use a serial interface. If you had Modbus Serial Server configured, this means that the device will act as a server and other services will not be able to use this serial connection. Since you are reading modbus data from other devices, you need to configure Modbus Serial Client (the RUT will send requests to the server).