RS232 conection issues TRB246 to CR350

Hi All,
I am trying to connect to a Campbell Scientific CR350 via RS232 (on Com2). The connection between the two works as a LAN connection (Ethernet cable connected from PC to TRB246, Serial connection from the TRB346 to the CR350), using this I can connect to the CR350 using Campbell Sci software (Dev config) As soon as I try to connect from the Mobile connection (I am using an APN which is setup and working and I can remotely connect to the Teltonika using the IP address) the connection does not work.

I have setup the “Over IP” to match the expected from the datalaooger and since i can connect through the LAN, I am confident the settings are correct. I just cant connect via the Cellualer IP connection.

Any help would be greatly appreciated.

Hi there,

As I’d like to look into this more, I’ve sent you a form to fill out so we can continue our conversation in private, to avoid accidentally leaking any sensitive information. In the Ticket ID field, simply enter the thread’s number, which is 14777.

Thank you,
M.

Issue has been resolved by adding the full IP filter address of 0.0.0.0/0

Regards,
M.