When using OPC-UA Client service at an TRB140 I am not aible to read a node at the server without error but when I am using Windows Software “Prosys OPC UA Client” I can read exactly the same node without any fault.
Could it be there is an bug when I have ID type “String” and the NodeId Identifier has spaces in the ID, for e.g. “Alarm window”?
Setting in nano /etc/config/opcua_client are the follow
config main ‘main’
option debug ‘0’
option enabled ‘1’
Apologies for the delay. To assist you further, could you please confirm whether this issue still persists on the latest firmware version (7.14.2) for the TRB140? If so, it would be very helpful if you could provide some debug logs so we can take a closer look at what’s happening on the device side.
You can enable debug mode for the OPC UA Client by connecting to the device via CLI and running the following commands:
/etc/init.d/opcua_client stop
opcua_client -D 9
This will start the OPC UA Client in debug mode and produce detailed logs. Please let it run for about a minute while the issue occurs, then press CTRL+C to stop the command. Afterward, copy the entire output and paste it either into a .txt file or within a spoiler in your reply.
Once debugging is complete, don’t forget to restart the service with
Before I update to branch “Latest” 7.14.3 which most is not same stable as branch “Mass production” 7.13.4 (Stable) is could you please confirm that there is a easy way to downgrade again to branch “Mass production”?
If you have a configuration backup made from 7.13.4, then downgrading from 7.14.3 back is straightforward; you can simply upload the firmware and restore your backup afterward.
However, if you don’t have a backup file from the previous firmware version, the downgrade process will reset the device to default settings once the older firmware is applied.
Furthermore, could you clarify the reason why you wish to downgrade? Are there any other, OPC-UA unrelated, issues noticed on 7.14.3?
… i just paste the content of the debug file as follow:
BusyBox v1.34.1 (2025-06-04 10:34:44 UTC) built-in shell (ash)
____ _ ___ ____
| _ \ _ _| |_ / _ \/ ___|
| |_) | | | | __| | | \___ \
| _ <| |_| | |_| |_| |___) |
|_| \_\\__,_|\__|\___/|____/
----------------------------------
Teltonika TRB1 series 2025
----------------------------------
Device: TRB140
Kernel: 5.4.292
Firmware: TRB1_R_00.07.15
Build: 18a177b964b
Build date: 2025-06-04 12:09:46
----------------------------------
root@TRB140:~# /etc/init.d/opcua_client stop
root@TRB140:~# opcua_client -D 9
src/log.c:58:log_init(): left
src/master.c:125:main(): log_level is 9
src/cfg.c:88:cfg_load_master_uci(): entered
src/cfg.c:134:cfg_load_master(): entered
src/cfg.c:204:cfg_load_server(): entered
src/cfg.c:295:cfg_load_server_security(): entered
src/cfg.c:384:cfg_load_server_security(): left
src/cfg.c:390:cfg_load_server_node(): entered
src/utl.c:87:utl_scan_node_id(): entered
src/utl.c:140:utl_scan_node_id(): left
src/cfg.c:428:cfg_load_server_node(): left
src/cfg.c:283:cfg_load_server(): left
src/cfg.c:192:cfg_load_master(): left
src/cfg.c:128:cfg_load_master_uci(): left
src/utl.c:439:utl_log_master(): entered
src/utl.c:445:utl_log_master(): main->enabled=1
src/utl.c:446:utl_log_master(): main->server_count=1
src/utl.c:447:utl_log_master(): main->value_group_count=0
src/utl.c:463:utl_log_server(): entered
src/utl.c:472:utl_log_server(): server('1')->enabled=1
src/utl.c:473:utl_log_server(): server('1')->section_name='1'
src/utl.c:474:utl_log_server(): server('1')->name='ClaireNeo'
src/utl.c:475:utl_log_server(): server('1')->url='opc.tcp://192.168.222.180:4840'
src/utl.c:476:utl_log_server(): server('1')->timeout=5000
src/utl.c:480:utl_log_server(): server('1')->identity.type='ANONYMOUS'
src/utl.c:488:utl_log_server(): server('1')->security.mode='NONE'
src/utl.c:499:utl_log_server(): server('1')->server_node_count=1
src/utl.c:510:utl_log_server_node(): entered
src/utl.c:521:utl_log_server_node(): server_node('2')->section_name='2'
src/utl.c:522:utl_log_server_node(): server_node('2')->name='AlarmWindow'
src/utl.c:524:utl_log_server_node(): server_node('2')->node=ns=1;s=Alarm Windows
src/utl.c:531:utl_log_server_node(): left
src/utl.c:505:utl_log_server(): left
src/utl.c:458:utl_log_master(): left
src/master.c:286:db_init(): entered
src/master.c:352:db_open(): entered
src/master.c:392:create_file(): entered
src/master.c:403:create_file(): left
src/master.c:386:db_open(): left
src/master.c:337:db_init(): left
src/master.c:409:handle_servers(): entered
src/utl.c:267:utl_connect_to_ua_server(): entered
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Starting the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): skip verifying ApplicationURI for the SecurityPolicy http://opcfoundation.org/UA/SecurityPolicy#None
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP | Open a connection to "192.168.222.180" on port 4840
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | New connection to "192.168.222.180" on port 4840
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Connecting, SessionState: Closed, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Opening a new connection
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Sent HEL message
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: HELSent, SessionState: Closed, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Allocate receive buffer
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Received message of size 28
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 0 | Process ACK message
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 0 | Generating new local nonce
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 0 | Requesting to open a SecureChannel
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Requesting to open a SecureChannel
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): OPN message sent
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: OPNSent, SessionState: Closed, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Allocate receive buffer
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Received message of size 135
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Verifying chunk signature
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Process OPN message
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Generating new local keys
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | SecureChannel opened with SecurityPolicy http://opcfoundation.org/UA/SecurityPolicy#None and a revised lifetime of 600.00s
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Sending request with RequestId 2 of type FindServersRequest
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Send from a symmetric message buffer of length 65536 a message of header+payload length of 99
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Send from a symmetric message buffer of length 65536 a message of length 99
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Open, SessionState: Closed, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Allocate receive buffer
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Received message of size 209
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Generating new remote keys
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Process MSG message with RequestId 2
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Decode a message of type FindServersResponse
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Received FindServersResponse
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Use the EndpointURL opc.tcp://berner_claire:4840 returned from FindServers
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Closing the channel
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Sending the CLO message
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Send from a symmetric message buffer of length 65536 a message of header+payload length of 57
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | SC 5 | Send from a symmetric message buffer of length 65536 a message of length 57
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Shutdown triggered
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Closing, SessionState: Closed, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Delayed closing of the connection
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 0 | SC 0 | Closed the SecureChannel
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): skip verifying ApplicationURI for the SecurityPolicy http://opcfoundation.org/UA/SecurityPolicy#None
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP | Open a connection to "192.168.222.180" on port 4840
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | New connection to "192.168.222.180" on port 4840
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Connecting, SessionState: Closed, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 8 | Socket closed
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Opening a new connection
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Sent HEL message
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: HELSent, SessionState: Closed, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Allocate receive buffer
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Received message of size 28
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 0 | Process ACK message
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 0 | Generating new local nonce
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 0 | Requesting to open a SecureChannel
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Requesting to open a SecureChannel
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): OPN message sent
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: OPNSent, SessionState: Closed, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Allocate receive buffer
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Received message of size 135
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Verifying chunk signature
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Process OPN message
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Generating new local keys
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | SecureChannel opened with SecurityPolicy http://opcfoundation.org/UA/SecurityPolicy#None and a revised lifetime of 600.00s
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Sending request with RequestId 5 of type GetEndpointsRequest
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of header+payload length of 97
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of length 97
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Open, SessionState: Closed, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Allocate receive buffer
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Received message of size 512
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Generating new remote keys
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Process MSG message with RequestId 5
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Decode a message of type GetEndpointsResponse
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Received GetEndpointsResponse
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Selected endpoint 0 in URL opc.tcp://berner_claire:4840 with SecurityMode None and SecurityPolicy http://opcfoundation.org/UA/SecurityPolicy#None
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Selected UserTokenPolicy open62541-anonymous-policy with UserTokenType Anonymous and SecurityPolicy http://opcfoundation.org/UA/SecurityPolicy#None
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Sending request with RequestId 6 of type CreateSessionRequest
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of header+payload length of 170
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of length 170
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Open, SessionState: CreateRequested, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Allocate receive buffer
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Received message of size 582
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Process MSG message with RequestId 6
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Decode a message of type CreateSessionResponse
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Sending request with RequestId 7 of type ActivateSessionRequest
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of header+payload length of 137
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of length 137
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Open, SessionState: Created, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Open, SessionState: ActivateRequested, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Allocate receive buffer
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Received message of size 96
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Process MSG message with RequestId 7
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Decode a message of type ActivateSessionResponse
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Open, SessionState: Activated, ConnectStatus: Good
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:329:utl_connect_to_ua_server(): left
src/master.c:430:handle_servers(): left
src/master.c:447:handle_value_groups(): entered
src/master.c:474:handle_value_groups(): left
src/ubus.c:173:ubus_server_object_init(): entered
src/ubus.c:202:ubus_server_object_init(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/master.c:480:cb_server(): entered
src/utl.c:362:utl_check_server(): entered
src/utl.c:379:utl_check_server(): channel_status=11 connection_status=0 session_status=4
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Internally check the the client state and required activities
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:384:utl_check_server(): UA_Client_run_iterate(): Good
src/utl.c:393:utl_check_server(): left
src/master.c:498:cb_server(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/ubus.c:6:ubus_status_cb(): entered
src/ubus.c:167:ubus_status_cb(): left
src/master.c:480:cb_server(): entered
src/utl.c:362:utl_check_server(): entered
src/utl.c:379:utl_check_server(): channel_status=11 connection_status=0 session_status=4
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Internally check the the client state and required activities
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:384:utl_check_server(): UA_Client_run_iterate(): Good
src/utl.c:393:utl_check_server(): left
src/master.c:498:cb_server(): left
src/master.c:480:cb_server(): entered
src/utl.c:362:utl_check_server(): entered
src/utl.c:379:utl_check_server(): channel_status=11 connection_status=0 session_status=4
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Internally check the the client state and required activities
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:384:utl_check_server(): UA_Client_run_iterate(): Good
src/utl.c:393:utl_check_server(): left
src/master.c:498:cb_server(): left
src/master.c:480:cb_server(): entered
src/utl.c:362:utl_check_server(): entered
src/utl.c:379:utl_check_server(): channel_status=11 connection_status=0 session_status=4
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Internally check the the client state and required activities
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:384:utl_check_server(): UA_Client_run_iterate(): Good
src/utl.c:393:utl_check_server(): left
src/master.c:498:cb_server(): left
^Csrc/master.c:202:signal_handler(): entered
src/master.c:204:signal_handler(): Signal received: 2
src/master.c:220:cleanup(): entered
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Sending request with RequestId 8 of type CloseSessionRequest
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of header+payload length of 75
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of length 75
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Internally check the the client state and required activities
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Activity on the socket
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Allocate receive buffer
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Received message of size 52
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Process MSG message with RequestId 8
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Decode a message of type CloseSessionResponse
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Closing the channel
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Sending the CLO message
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of header+payload length of 57
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | SC 6 | Send from a symmetric message buffer of length 65536 a message of length 57
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Attempting to send
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Shutdown triggered
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Iterate the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Process delayed callbacks
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Delayed closing of the connection
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client network callback
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 0 | SC 0 | Closed the SecureChannel
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client connect iterate
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Client Status: ChannelState: Fresh, SessionState: Closed, ConnectStatus: BadConnectionClosed
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP 9 | Socket closed
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): Stopping the EventLoop
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): UDP | Shutting down the ConnectionManager
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): UDP | All sockets closed, the EventLoop has stopped
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP | Shutting down the ConnectionManager
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): TCP | All sockets closed, the EventLoop has stopped
src/utl.c:894:ua_log(): left
src/utl.c:884:ua_log(): entered
src/utl.c:899:ua_level_to_log_level(): entered
src/utl.c:913:ua_level_to_log_level(): left
src/utl.c:891:ua_log(): The EventLoop has stopped
src/utl.c:894:ua_log(): left
root@TRB140:~#
In this case, if you still notice any issues regarding the OPC-UA client, I believe, to assist you effectively, we’ll need to continue this process privately. You should find a support request form in the inbox of the email address you used for your forum registration. Kindly fill out the form, and please reference Ticket ID: 13387 when submitting it. Once the form is completed, we’ll contact you directly via email to investigate the issue in detail and help work towards a solution.