Modbus TCP on a EVC12 - is it possible?
Recently an installer installed an EVC12 in my garage - mistakenly, as I was expecting it to be an EVC2x and had a load manager prepared to handle Modbus TCP.
In the EVC12 I see Load Management only via Modbus RTU; is it at all possible to enable Modbus TCP?
Thanks in advance,
Nuno
Unfortunately, Modbus TCP is not supported on the EVC12. The EVC12 only supports Load Management via Modbus RTU (RS485), and there is currently no option to enable Modbus TCP through settings or a firmware update.
If your EMS or load management system requires Modbus TCP, you would need to use a Modbus TCP-to-RTU gateway (provided your controller supports this setup) or consider replacing the charger with an EVC2/EVC2x, which supports Modbus TCP communication.
So, if your installation was designed around direct Modbus TCP integration, the EVC12 will not be able to provide that functionality natively.
Kindest regards,
Džiugas-Teltonika
Thank you for your swift reply. I will then go for a TCP-to-RTU gateway to set it all in place.
Thanks again,
Nuno