Errors Nr. 1 and Nr. 2 after month of flawless work

Hello,

My client shared that his TeltoCharge 11 kW charging station EVC111 started to show top two error indicators after month of use. He tried restarting the station, that didin’t help. He also said that sometimes EV starts to charge but just for 10-15 seconds and only at 2kw power and then stops again. He tried other stations in the city and they worked well. How to troubleshoot the problem?

Hi,

there’s a lot that can go wrong. Would it be possible for the client to send a troubleshoot file to support.energy@teltonika.lt as per these instructions:

Here is the log from the file.

-----BEGIN EVENT LOG-----
2025-07-11T20:39:03+03:00 Voltage Input fail
2025-07-11T20:39:03+03:00 Voltage Output fail
2025-07-11T22:08:52+03:00 EV disconnected
2025-07-11T22:08:52+03:00 EVSE ready
2025-07-11T22:08:55+03:00 EV connected
2025-07-11T22:09:00+03:00 Start charging
2025-07-11T22:09:06+03:00 Voltage Input fail
2025-07-11T22:09:06+03:00 Voltage Output fail
2025-07-11T22:09:09+03:00 EVSE ready
2025-07-11T22:09:15+03:00 Start charging
2025-07-11T22:09:15+03:00 Cable locked
2025-07-11T22:09:16+03:00 Cable unlocked
2025-07-11T22:09:32+03:00 Voltage Input fail
2025-07-11T22:09:32+03:00 Voltage Output fail
2025-07-11T22:09:35+03:00 EVSE ready
2025-07-11T22:09:41+03:00 Start charging
2025-07-11T22:10:21+03:00 Charging done
2025-07-11T22:10:23+03:00 Start charging
2025-07-11T22:10:25+03:00 Voltage Input fail
2025-07-11T22:10:25+03:00 Voltage Output fail
2025-07-11T22:10:28+03:00 EVSE ready
2025-07-11T22:10:33+03:00 Start charging
2025-07-11T22:11:09+03:00 Charging done
2025-07-11T22:11:11+03:00 Start charging
2025-07-11T22:11:15+03:00 Voltage Input fail
2025-07-11T22:11:15+03:00 Voltage Output fail
2025-07-11T22:12:14+03:00 EV disconnected
2025-07-11T22:12:14+03:00 EVSE ready
2025-07-11T22:12:19+03:00 EV connected
2025-07-11T22:12:24+03:00 Start charging
2025-07-11T22:13:14+03:00 Charging done
2025-07-11T22:13:16+03:00 Start charging
2025-07-11T22:13:25+03:00 Voltage Input fail
2025-07-11T22:13:25+03:00 Voltage Output fail
2025-07-11T22:13:28+03:00 EVSE ready
2025-07-11T22:13:33+03:00 Start charging
2025-07-11T22:13:40+03:00 Voltage Input fail
2025-07-11T22:13:40+03:00 Voltage Output fail
2025-07-11T22:13:43+03:00 EVSE ready
2025-07-11T22:13:48+03:00 Start charging
2025-07-11T22:14:15+03:00 Voltage Input fail
2025-07-11T22:14:15+03:00 Voltage Output fail
2025-07-11T22:14:18+03:00 EVSE ready
2025-07-11T22:14:24+03:00 Start charging
2025-07-11T22:15:00+03:00 Charging done
2025-07-11T22:15:02+03:00 Start charging
2025-07-11T22:15:05+03:00 Voltage Input fail
2025-07-11T22:15:05+03:00 Voltage Output fail
2025-07-11T22:15:45+03:00 EV disconnected
2025-07-11T22:15:45+03:00 EVSE ready
2025-07-11T22:15:52+03:00 EV connected
2025-07-11T22:15:56+03:00 Start charging
2025-07-11T22:15:58+03:00 Voltage Input fail
2025-07-11T22:15:58+03:00 Voltage Output fail
2025-07-11T22:16:01+03:00 EVSE ready
2025-07-11T22:16:03+03:00 EV disconnected
2025-07-11T22:16:10+03:00 EV connected
2025-07-11T22:16:14+03:00 Start charging
2025-07-11T22:16:16+03:00 Voltage Input fail
2025-07-11T22:16:16+03:00 Voltage Output fail
2025-07-11T22:16:19+03:00 EVSE ready
2025-07-11T22:16:24+03:00 Start charging
2025-07-11T22:17:08+03:00 Charging done
2025-07-11T22:17:10+03:00 Start charging
2025-07-11T22:17:12+03:00 Voltage Input fail
2025-07-11T22:17:12+03:00 Voltage Output fail
2025-07-11T22:17:15+03:00 EVSE ready
2025-07-11T22:17:21+03:00 Start charging
2025-07-11T22:18:07+03:00 Charging done
2025-07-11T22:18:09+03:00 Start charging
2025-07-11T22:18:11+03:00 Voltage Input fail
2025-07-11T22:18:11+03:00 Voltage Output fail
2025-07-11T22:18:14+03:00 EVSE ready
2025-07-11T22:18:19+03:00 Start charging
2025-07-11T22:18:58+03:00 Charging done
2025-07-11T22:19:00+03:00 Start charging
2025-07-11T22:19:02+03:00 Voltage Input fail
2025-07-11T22:19:02+03:00 Voltage Output fail
2025-07-11T22:20:51+03:00 EV disconnected
2025-07-11T22:20:51+03:00 EVSE ready
2025-07-11T22:20:58+03:00 EV connected
2025-07-11T22:21:02+03:00 Start charging
2025-07-11T22:21:09+03:00 Voltage Input fail
2025-07-11T22:21:09+03:00 Voltage Output fail
2025-07-11T22:21:12+03:00 EVSE ready
2025-07-11T22:21:18+03:00 Start charging
2025-07-11T22:21:56+03:00 Charging done
2025-07-11T22:21:58+03:00 Start charging
2025-07-11T22:22:03+03:00 Voltage Input fail
2025-07-11T22:22:03+03:00 Voltage Output fail
2025-07-11T22:22:06+03:00 EVSE ready
2025-07-11T22:22:12+03:00 Start charging
2025-07-11T22:23:25+03:00 Charging done
2025-07-11T22:23:27+03:00 Start charging
2025-07-11T22:23:32+03:00 Voltage Input fail
2025-07-11T22:23:32+03:00 Voltage Output fail
2025-07-11T22:23:35+03:00 EVSE ready
2025-07-11T22:23:42+03:00 Start charging
2025-07-11T22:23:48+03:00 Voltage Input fail
2025-07-11T22:23:48+03:00 Voltage Output fail
2025-07-11T22:25:39+03:00 EV disconnected
2025-07-11T22:25:39+03:00 EVSE ready
2025-07-11T22:25:44+03:00 EV connected
2025-07-11T22:25:48+03:00 Start charging
2025-07-11T22:25:50+03:00 Voltage Output fail
2025-07-11T22:25:51+03:00 Voltage Input fail
2025-07-11T22:25:53+03:00 EVSE ready
2025-07-11T22:25:59+03:00 Start charging
2025-07-11T22:26:01+03:00 Voltage Input fail
2025-07-11T22:26:01+03:00 Voltage Output fail
2025-07-11T22:26:04+03:00 EVSE ready
2025-07-11T22:26:09+03:00 Start charging
2025-07-11T22:27:04+03:00 Charging done
2025-07-11T22:27:06+03:00 Start charging
2025-07-11T22:27:15+03:00 Voltage Input fail
2025-07-11T22:27:15+03:00 Voltage Output fail
2025-07-11T22:27:18+03:00 EVSE ready
2025-07-11T22:27:24+03:00 Start charging
2025-07-11T22:28:01+03:00 Charging done
2025-07-11T22:28:03+03:00 Start charging
2025-07-11T22:28:18+03:00 Voltage Input fail
2025-07-11T22:28:18+03:00 Voltage Output fail
2025-07-11T22:29:03+03:00 EV disconnected
2025-07-11T22:29:03+03:00 EVSE ready
2025-07-11T22:30:56+03:00 System started
2025-07-11T22:31:39+03:00 EV connected
2025-07-11T22:32:10+03:00 Start charging
2025-07-11T22:32:12+03:00 Voltage Input fail
2025-07-11T22:32:12+03:00 Voltage Output fail
2025-07-11T22:32:15+03:00 EVSE ready
2025-07-11T22:32:20+03:00 Start charging
2025-07-11T22:32:26+03:00 Voltage Input fail
2025-07-11T22:32:26+03:00 Voltage Output fail
2025-07-11T22:32:29+03:00 EVSE ready
2025-07-11T22:32:35+03:00 Start charging
2025-07-11T22:32:41+03:00 Voltage Input fail
2025-07-11T22:32:41+03:00 Voltage Output fail
2025-07-11T22:32:44+03:00 EVSE ready
2025-07-11T22:32:50+03:00 Start charging
2025-07-11T22:33:08+03:00 Voltage Input fail
2025-07-11T22:33:08+03:00 Voltage Output fail
2025-07-11T22:33:51+03:00 EV disconnected
2025-07-11T22:33:51+03:00 EVSE ready
2025-07-11T22:34:00+03:00 EV connected
2025-07-11T22:34:04+03:00 Start charging
2025-07-11T22:34:10+03:00 Voltage Input fail
2025-07-11T22:34:10+03:00 Voltage Output fail
2025-07-11T22:34:13+03:00 EVSE ready
2025-07-11T22:34:19+03:00 Start charging
2025-07-11T22:34:19+03:00 Cable locked
2025-07-11T22:34:20+03:00 Cable unlocked
2025-07-11T22:34:26+03:00 Voltage Input fail
2025-07-11T22:34:26+03:00 Voltage Output fail
2025-07-11T22:34:29+03:00 EVSE ready
2025-07-11T22:34:34+03:00 Start charging
2025-07-11T22:34:34+03:00 Cable locked
2025-07-11T22:34:35+03:00 Cable unlocked
2025-07-11T22:34:36+03:00 Voltage Input fail
2025-07-11T22:34:36+03:00 Voltage Output fail
2025-07-11T22:34:39+03:00 EVSE ready
2025-07-11T22:34:45+03:00 Start charging
2025-07-11T22:34:47+03:00 Voltage Input fail
2025-07-11T22:34:47+03:00 Voltage Output fail
2025-07-11T22:35:26+03:00 EV disconnected
2025-07-11T22:35:26+03:00 EVSE ready
2025-07-11T22:35:34+03:00 EV connected
2025-07-11T22:35:38+03:00 Start charging
2025-07-11T22:35:44+03:00 Voltage Input fail
2025-07-11T22:35:44+03:00 Voltage Output fail
2025-07-11T22:35:47+03:00 EVSE ready
2025-07-11T22:35:52+03:00 Start charging
2025-07-11T22:36:04+03:00 Voltage Input fail
2025-07-11T22:36:04+03:00 Voltage Output fail
2025-07-11T22:36:07+03:00 EVSE ready
2025-07-11T22:36:12+03:00 Start charging
2025-07-11T22:37:01+03:00 Charging done
2025-07-11T22:37:03+03:00 Start charging
2025-07-11T22:37:09+03:00 Voltage Input fail
2025-07-11T22:37:09+03:00 Voltage Output fail
2025-07-11T22:37:12+03:00 EVSE ready
2025-07-11T22:37:17+03:00 Start charging
2025-07-11T23:06:13+03:00 Charging done
2025-07-11T23:06:14+03:00 Start charging
2025-07-11T23:06:40+03:00 Charging done
2025-07-11T23:06:42+03:00 Start charging
2025-07-11T23:06:54+03:00 Voltage Input fail
2025-07-11T23:06:54+03:00 Voltage Output fail
2025-07-11T23:15:59+03:00 EVSE ready
2025-07-11T23:16:10+03:00 Start charging
2025-07-11T23:16:18+03:00 Voltage Output fail
2025-07-11T23:21:00+03:00 EVSE ready
2025-07-11T23:21:13+03:00 Start charging
2025-07-11T23:21:19+03:00 Voltage Output fail
2025-07-11T23:26:43+03:00 EV disconnected
2025-07-11T23:26:43+03:00 EVSE ready
2025-07-11T23:26:47+03:00 EV connected
2025-07-11T23:26:51+03:00 Start charging
2025-07-11T23:46:29+03:00 Charging done
2025-07-11T23:46:30+03:00 EV disconnected
2025-07-11T23:46:34+03:00 EV connected
2025-07-11T23:46:39+03:00 Start charging
2025-07-11T23:52:05+03:00 Charging done
2025-07-11T23:52:07+03:00 Start charging
2025-07-11T23:52:07+03:00 Cable locked
2025-07-11T23:52:08+03:00 Cable unlocked
2025-07-11T23:52:23+03:00 Voltage Input fail
2025-07-11T23:52:23+03:00 Voltage Output fail
2025-07-11T23:52:26+03:00 EVSE ready
2025-07-11T23:52:32+03:00 Start charging
2025-07-11T23:53:10+03:00 Charging done
2025-07-11T23:53:12+03:00 Start charging
2025-07-11T23:53:15+03:00 Voltage Input fail
2025-07-11T23:53:15+03:00 Voltage Output fail
2025-07-11T23:53:18+03:00 EVSE ready
2025-07-11T23:53:23+03:00 Start charging
2025-07-11T23:53:25+03:00 Voltage Input fail
2025-07-11T23:53:25+03:00 Voltage Output fail
2025-07-11T23:53:28+03:00 EVSE ready
2025-07-11T23:53:34+03:00 Start charging
2025-07-11T23:54:12+03:00 Charging done
2025-07-11T23:54:14+03:00 Start charging
2025-07-11T23:54:19+03:00 Voltage Input fail
2025-07-11T23:54:19+03:00 Voltage Output fail
2025-07-11T23:55:47+03:00 EV disconnected
2025-07-11T23:55:47+03:00 EVSE ready
2025-07-11T23:55:53+03:00 EV connected
2025-07-11T23:55:58+03:00 Start charging
2025-07-11T23:56:04+03:00 Voltage Input fail
2025-07-11T23:56:04+03:00 Voltage Output fail
2025-07-11T23:56:07+03:00 EVSE ready
2025-07-11T23:56:12+03:00 Start charging
2025-07-11T23:56:56+03:00 Charging done
2025-07-11T23:56:58+03:00 Start charging
2025-07-11T23:57:00+03:00 Voltage Input fail
2025-07-11T23:57:00+03:00 Voltage Output fail
2025-07-11T23:57:03+03:00 EVSE ready
2025-07-11T23:57:08+03:00 Start charging
2025-07-11T23:57:15+03:00 Voltage Input fail
2025-07-11T23:57:15+03:00 Voltage Output fail
2025-07-11T23:57:18+03:00 EVSE ready
2025-07-11T23:57:24+03:00 Start charging
2025-07-11T23:57:26+03:00 Voltage Input fail
2025-07-11T23:57:26+03:00 Voltage Output fail
2025-07-11T23:57:43+03:00 EV disconnected
2025-07-11T23:57:43+03:00 EVSE ready
2025-07-11T23:57:47+03:00 EV connected
2025-07-11T23:57:51+03:00 Start charging
2025-07-11T23:57:53+03:00 Voltage Input fail
2025-07-11T23:57:53+03:00 Voltage Output fail
2025-07-11T23:57:56+03:00 EVSE ready
2025-07-11T23:58:01+03:00 Start charging
2025-07-11T23:58:44+03:00 Charging done
2025-07-11T23:58:46+03:00 Start charging
2025-07-11T23:58:46+03:00 Cable locked
2025-07-11T23:58:47+03:00 Cable unlocked
2025-07-11T23:58:48+03:00 Voltage Input fail
2025-07-11T23:58:48+03:00 Voltage Output fail
2025-07-11T23:58:51+03:00 EVSE ready
2025-07-11T23:58:56+03:00 Start charging
2025-07-11T23:59:32+03:00 Charging done
2025-07-11T23:59:34+03:00 Start charging
2025-07-11T23:59:43+03:00 Voltage Input fail
2025-07-11T23:59:43+03:00 Voltage Output fail
2025-07-11T23:59:46+03:00 EVSE ready
2025-07-11T23:59:52+03:00 Start charging
2025-07-12T00:00:31+03:00 Charging done
2025-07-12T00:00:33+03:00 Start charging
2025-07-12T00:00:43+03:00 Voltage Input fail
2025-07-12T00:00:43+03:00 Voltage Output fail
2025-07-12T00:01:17+03:00 EV disconnected
2025-07-12T00:01:17+03:00 EVSE ready
2025-07-12T00:01:21+03:00 EV connected
2025-07-12T00:01:25+03:00 Start charging
2025-07-12T00:01:27+03:00 Voltage Input fail
2025-07-12T00:01:27+03:00 Voltage Output fail
2025-07-12T00:01:30+03:00 EVSE ready
2025-07-12T00:01:35+03:00 Start charging
2025-07-12T00:02:13+03:00 Charging done
2025-07-12T00:02:16+03:00 Start charging
2025-07-12T00:02:25+03:00 Voltage Input fail
2025-07-12T00:02:25+03:00 Voltage Output fail
2025-07-12T00:02:28+03:00 EVSE ready
2025-07-12T00:02:33+03:00 Start charging
2025-07-12T00:03:07+03:00 Voltage Input fail
2025-07-12T00:03:07+03:00 Voltage Output fail
2025-07-12T00:03:10+03:00 EVSE ready
2025-07-12T00:03:15+03:00 Start charging
2025-07-12T00:03:20+03:00 Charging done
2025-07-12T00:03:21+03:00 EV disconnected
2025-07-12T00:03:24+03:00 EV connected
2025-07-12T00:03:28+03:00 Start charging
2025-07-12T00:04:04+03:00 Charging done
2025-07-12T00:04:06+03:00 Start charging
2025-07-12T00:04:11+03:00 Voltage Input fail
2025-07-12T00:04:11+03:00 Voltage Output fail
2025-07-12T00:04:14+03:00 EVSE ready
2025-07-12T00:04:20+03:00 Start charging
2025-07-12T00:05:14+03:00 Charging done
2025-07-12T00:05:16+03:00 Start charging
2025-07-12T00:05:18+03:00 Voltage Input fail
2025-07-12T00:05:18+03:00 Voltage Output fail
2025-07-12T00:05:20+03:00 EVSE ready
2025-07-12T00:05:26+03:00 Start charging
2025-07-12T00:05:44+03:00 Voltage Input fail
2025-07-12T00:05:44+03:00 Voltage Output fail
2025-07-12T00:05:47+03:00 EVSE ready
2025-07-12T00:05:53+03:00 Start charging
2025-07-12T00:06:28+03:00 Charging done
2025-07-12T00:06:31+03:00 Start charging
2025-07-12T00:06:52+03:00 Voltage Input fail
2025-07-12T00:06:52+03:00 Voltage Output fail
2025-07-12T00:07:34+03:00 EV disconnected
2025-07-12T00:07:35+03:00 EVSE ready
2025-07-12T00:07:42+03:00 EV connected
2025-07-12T00:07:47+03:00 Start charging
2025-07-12T00:07:47+03:00 Cable locked
2025-07-12T00:07:49+03:00 Voltage Output fail
2025-07-12T00:07:49+03:00 Cable unlocked
2025-07-12T00:07:50+03:00 Voltage Input fail
2025-07-12T00:07:52+03:00 EVSE ready
2025-07-12T00:07:58+03:00 Start charging
2025-07-12T00:07:58+03:00 Cable locked
2025-07-12T00:07:59+03:00 Cable unlocked
2025-07-12T00:08:00+03:00 Voltage Input fail
2025-07-12T00:08:00+03:00 Voltage Output fail
2025-07-12T00:08:03+03:00 EVSE ready
2025-07-12T00:08:08+03:00 Start charging
2025-07-12T00:08:24+03:00 Voltage Input fail
2025-07-12T00:08:24+03:00 Voltage Output fail
2025-07-12T00:08:26+03:00 EVSE ready
2025-07-12T00:08:33+03:00 Charging done
2025-07-12T00:08:35+03:00 EV disconnected
2025-07-12T00:08:37+03:00 EV connected
2025-07-12T00:08:42+03:00 Start charging
2025-07-12T00:08:50+03:00 Voltage Input fail
2025-07-12T00:08:50+03:00 Voltage Output fail
2025-07-12T00:08:53+03:00 EVSE ready
2025-07-12T00:08:59+03:00 Start charging
2025-07-12T00:09:45+03:00 Charging done
2025-07-12T00:09:47+03:00 Start charging
2025-07-12T00:09:47+03:00 Cable locked
2025-07-12T00:09:48+03:00 Cable unlocked
2025-07-12T00:09:49+03:00 Voltage Input fail
2025-07-12T00:09:49+03:00 Voltage Output fail
2025-07-12T00:09:52+03:00 EVSE ready
2025-07-12T00:09:57+03:00 Start charging
2025-07-12T00:10:00+03:00 Voltage Input fail
2025-07-12T00:10:00+03:00 Voltage Output fail
2025-07-12T00:10:03+03:00 EVSE ready
2025-07-12T00:10:08+03:00 Start charging
2025-07-12T00:10:08+03:00 Cable locked
2025-07-12T00:10:09+03:00 Cable unlocked
2025-07-12T00:10:14+03:00 Voltage Input fail
2025-07-12T00:10:14+03:00 Voltage Output fail
2025-07-12T00:11:11+03:00 EV disconnected
2025-07-12T00:11:11+03:00 EVSE ready
2025-07-12T00:11:14+03:00 EV connected
2025-07-12T00:11:18+03:00 Start charging
2025-07-12T00:11:18+03:00 Cable locked
2025-07-12T00:11:19+03:00 Cable unlocked
2025-07-12T00:11:20+03:00 Voltage Input fail
2025-07-12T00:11:20+03:00 Voltage Output fail
2025-07-12T00:11:23+03:00 EVSE ready
2025-07-12T00:11:29+03:00 Start charging
2025-07-12T00:11:34+03:00 Voltage Input fail
2025-07-12T00:11:34+03:00 Voltage Output fail
2025-07-12T00:11:38+03:00 EVSE ready
2025-07-12T00:11:44+03:00 Start charging
2025-07-12T00:11:46+03:00 Voltage Input fail
2025-07-12T00:11:46+03:00 Voltage Output fail
2025-07-12T00:11:49+03:00 EVSE ready
2025-07-12T00:11:54+03:00 Start charging
2025-07-12T00:11:54+03:00 Cable locked
2025-07-12T00:11:56+03:00 Voltage Input fail
2025-07-12T00:11:56+03:00 Voltage Output fail
2025-07-12T00:11:56+03:00 Cable unlocked
2025-07-12T00:12:11+03:00 EV disconnected
2025-07-12T00:12:11+03:00 EVSE ready
2025-07-12T00:12:17+03:00 EV connected
2025-07-12T00:12:22+03:00 Start charging
2025-07-12T00:12:24+03:00 Voltage Input fail
2025-07-12T00:12:24+03:00 Voltage Output fail
2025-07-12T00:12:27+03:00 EVSE ready
2025-07-12T00:12:32+03:00 Start charging
2025-07-12T00:13:07+03:00 Charging done
2025-07-12T00:13:10+03:00 Start charging
2025-07-12T00:13:12+03:00 Voltage Input fail
2025-07-12T00:13:12+03:00 Voltage Output fail
2025-07-12T00:13:15+03:00 EVSE ready
2025-07-12T00:13:20+03:00 Start charging
2025-07-12T00:13:56+03:00 Charging done
2025-07-12T00:13:58+03:00 Start charging
2025-07-12T00:14:00+03:00 Voltage Input fail
2025-07-12T00:14:00+03:00 Voltage Output fail
2025-07-12T00:14:03+03:00 EVSE ready
2025-07-12T00:14:08+03:00 Start charging
2025-07-12T00:14:10+03:00 Voltage Input fail
2025-07-12T00:14:10+03:00 Voltage Output fail
2025-07-12T00:14:46+03:00 EV disconnected
2025-07-12T00:14:47+03:00 EVSE ready
2025-07-12T00:14:49+03:00 EV connected
2025-07-12T00:14:54+03:00 Start charging
2025-07-12T00:14:56+03:00 Voltage Input fail
2025-07-12T00:14:56+03:00 Voltage Output fail
2025-07-12T00:15:00+03:00 EVSE ready
2025-07-12T00:15:05+03:00 Start charging
2025-07-12T00:16:14+03:00 Charging done
2025-07-12T00:16:16+03:00 Start charging
2025-07-12T00:16:18+03:00 Voltage Input fail
2025-07-12T00:16:18+03:00 Voltage Output fail
2025-07-12T00:16:21+03:00 EVSE ready
2025-07-12T00:16:26+03:00 Start charging
2025-07-12T00:16:28+03:00 Voltage Output fail
2025-07-12T00:16:29+03:00 Voltage Input fail
2025-07-12T00:16:31+03:00 EVSE ready
2025-07-12T00:16:37+03:00 Start charging
2025-07-12T00:17:44+03:00 Charging done
2025-07-12T00:17:46+03:00 Start charging
2025-07-12T00:17:49+03:00 Voltage Input fail
2025-07-12T00:17:49+03:00 Voltage Output fail
2025-07-12T00:27:14+03:00 EVSE ready
2025-07-12T00:27:26+03:00 Start charging
2025-07-12T00:27:30+03:00 Voltage Input fail
2025-07-12T00:27:30+03:00 Voltage Output fail
2025-07-12T00:37:14+03:00 EVSE ready
2025-07-12T00:37:25+03:00 Start charging
2025-07-12T00:37:37+03:00 Voltage Input fail
2025-07-12T00:37:37+03:00 Voltage Output fail
2025-07-12T02:37:14+03:00 EVSE ready
2025-07-12T02:37:27+03:00 Start charging
2025-07-12T02:37:39+03:00 Voltage Input fail
2025-07-12T02:37:39+03:00 Voltage Output fail
2025-07-12T04:37:15+03:00 EVSE ready
2025-07-12T04:37:27+03:00 Start charging
2025-07-12T04:37:27+03:00 Cable locked
2025-07-12T04:37:28+03:00 Cable unlocked
2025-07-12T04:37:55+03:00 Voltage Input fail
2025-07-12T04:37:55+03:00 Voltage Output fail
2025-07-12T04:57:44+03:00 EV disconnected
2025-07-12T04:57:44+03:00 EVSE ready
2025-07-12T04:57:47+03:00 EV connected
2025-07-12T04:57:52+03:00 Start charging
2025-07-12T04:58:00+03:00 Voltage Input fail
2025-07-12T04:58:00+03:00 Voltage Output fail
2025-07-12T04:58:03+03:00 EVSE ready
2025-07-12T04:58:08+03:00 Start charging
2025-07-12T04:58:10+03:00 Voltage Output fail
2025-07-12T04:58:12+03:00 Voltage Input fail
2025-07-12T04:58:15+03:00 EVSE ready
2025-07-12T04:58:20+03:00 Start charging
2025-07-12T04:58:22+03:00 Voltage Input fail
2025-07-12T04:58:22+03:00 Voltage Output fail
2025-07-12T04:58:25+03:00 EVSE ready
2025-07-12T04:58:31+03:00 Start charging
2025-07-12T04:58:33+03:00 Charging done
2025-07-12T04:58:35+03:00 EV disconnected
2025-07-12T04:58:44+03:00 EV connected
2025-07-12T04:58:49+03:00 Start charging
2025-07-12T04:59:10+03:00 Voltage Input fail
2025-07-12T04:59:10+03:00 Voltage Output fail
2025-07-12T04:59:13+03:00 EVSE ready
2025-07-12T04:59:19+03:00 Start charging
2025-07-12T04:59:57+03:00 Charging done
2025-07-12T04:59:59+03:00 Start charging
2025-07-12T05:00:28+03:00 Voltage Input fail
2025-07-12T05:00:28+03:00 Voltage Output fail
2025-07-12T05:00:31+03:00 EVSE ready
2025-07-12T05:00:36+03:00 Start charging
2025-07-12T05:00:36+03:00 Cable locked
2025-07-12T05:00:38+03:00 Cable unlocked
2025-07-12T05:00:45+03:00 Voltage Input fail
2025-07-12T05:00:45+03:00 Voltage Output fail
2025-07-12T05:00:48+03:00 EVSE ready
2025-07-12T05:00:54+03:00 Start charging
2025-07-12T05:01:32+03:00 Charging done
2025-07-12T05:01:34+03:00 Start charging
2025-07-12T05:01:42+03:00 Voltage Input fail
2025-07-12T05:01:42+03:00 Voltage Output fail
2025-07-12T05:01:58+03:00 EV disconnected
2025-07-12T05:01:58+03:00 EVSE ready
2025-07-12T05:02:06+03:00 EV connected
2025-07-12T05:02:11+03:00 Start charging
2025-07-12T05:02:18+03:00 Voltage Input fail
2025-07-12T05:02:18+03:00 Voltage Output fail
2025-07-12T05:02:21+03:00 EVSE ready
2025-07-12T05:02:26+03:00 Start charging
2025-07-12T05:02:36+03:00 Voltage Input fail
2025-07-12T05:02:36+03:00 Voltage Output fail
2025-07-12T05:02:39+03:00 EVSE ready
2025-07-12T05:02:44+03:00 Start charging
2025-07-12T05:03:20+03:00 Charging done
2025-07-12T05:03:22+03:00 Start charging
2025-07-12T05:03:27+03:00 Voltage Input fail
2025-07-12T05:03:27+03:00 Voltage Output fail
2025-07-12T05:03:30+03:00 EVSE ready
2025-07-12T05:03:36+03:00 Start charging
2025-07-12T05:04:11+03:00 Charging done
2025-07-12T05:04:14+03:00 Start charging
2025-07-12T05:04:19+03:00 Voltage Input fail
2025-07-12T05:04:19+03:00 Voltage Output fail
2025-07-12T05:04:53+03:00 EV disconnected
2025-07-12T05:04:53+03:00 EVSE ready
2025-07-12T05:05:07+03:00 EV connected
2025-07-12T05:05:12+03:00 Start charging
2025-07-12T05:05:18+03:00 Voltage Input fail
2025-07-12T05:05:18+03:00 Voltage Output fail
2025-07-12T05:05:21+03:00 EVSE ready
2025-07-12T05:05:26+03:00 Start charging
2025-07-12T05:06:32+03:00 Charging done
2025-07-12T05:06:34+03:00 Start charging
2025-07-12T05:07:03+03:00 Voltage Input fail
2025-07-12T05:07:03+03:00 Voltage Output fail
2025-07-12T05:07:06+03:00 EVSE ready
2025-07-12T05:07:12+03:00 Start charging
2025-07-12T05:07:18+03:00 Voltage Input fail
2025-07-12T05:07:18+03:00 Voltage Output fail
2025-07-12T05:07:21+03:00 EVSE ready
2025-07-12T05:07:26+03:00 Start charging
2025-07-12T05:07:32+03:00 Voltage Input fail
2025-07-12T05:07:32+03:00 Voltage Output fail
2025-07-12T05:09:41+03:00 EV disconnected
2025-07-12T05:09:41+03:00 EVSE ready
2025-07-12T05:09:48+03:00 EV connected
2025-07-12T05:09:53+03:00 Start charging
2025-07-12T05:09:59+03:00 Voltage Input fail
2025-07-12T05:09:59+03:00 Voltage Output fail
2025-07-12T05:10:02+03:00 EVSE ready
2025-07-12T05:10:07+03:00 Start charging
2025-07-12T05:10:35+03:00 Voltage Input fail
2025-07-12T05:10:35+03:00 Voltage Output fail
2025-07-12T05:10:39+03:00 EVSE ready
2025-07-12T05:10:45+03:00 Start charging
2025-07-12T05:10:47+03:00 Voltage Input fail
2025-07-12T05:10:47+03:00 Voltage Output fail
2025-07-12T05:10:50+03:00 EVSE ready
2025-07-12T05:10:55+03:00 Start charging
2025-07-12T05:10:57+03:00 Voltage Input fail
2025-07-12T05:10:57+03:00 Voltage Output fail
2025-07-12T05:11:18+03:00 EV disconnected
2025-07-12T05:11:18+03:00 EVSE ready
2025-07-12T05:11:33+03:00 EV connected
2025-07-12T05:11:38+03:00 Start charging
2025-07-12T05:11:46+03:00 Voltage Input fail
2025-07-12T05:11:46+03:00 Voltage Output fail
2025-07-12T05:11:49+03:00 EVSE ready
2025-07-12T05:11:55+03:00 Start charging
2025-07-12T05:12:01+03:00 Voltage Input fail
2025-07-12T05:12:01+03:00 Voltage Output fail
2025-07-12T05:12:05+03:00 EVSE ready
2025-07-12T05:12:10+03:00 Start charging
2025-07-12T05:12:12+03:00 Voltage Input fail
2025-07-12T05:12:12+03:00 Voltage Output fail
2025-07-12T05:12:15+03:00 EVSE ready
2025-07-12T05:12:21+03:00 Start charging
2025-07-12T05:12:21+03:00 Cable locked
2025-07-12T05:12:22+03:00 Cable unlocked
2025-07-12T05:12:26+03:00 Voltage Input fail
2025-07-12T05:12:26+03:00 Voltage Output fail
2025-07-12T05:13:10+03:00 EV disconnected
2025-07-12T05:13:10+03:00 EVSE ready
2025-07-12T05:13:14+03:00 EV connected
2025-07-12T05:13:19+03:00 Start charging
2025-07-12T05:13:28+03:00 Voltage Input fail
2025-07-12T05:13:28+03:00 Voltage Output fail
2025-07-12T05:13:30+03:00 EVSE ready
2025-07-12T05:13:37+03:00 Start charging
2025-07-12T05:13:43+03:00 Voltage Input fail
2025-07-12T05:13:43+03:00 Voltage Output fail
2025-07-12T05:13:46+03:00 EVSE ready
2025-07-12T05:13:51+03:00 Start charging
2025-07-12T05:13:51+03:00 Cable locked
2025-07-12T05:13:53+03:00 Cable unlocked
2025-07-12T05:14:03+03:00 Voltage Input fail
2025-07-12T05:14:03+03:00 Voltage Output fail
2025-07-12T05:14:06+03:00 EVSE ready
2025-07-12T05:14:11+03:00 Start charging
2025-07-12T05:14:11+03:00 Cable locked
2025-07-12T05:14:12+03:00 Cable unlocked
2025-07-12T05:14:20+03:00 Voltage Input fail
2025-07-12T05:14:20+03:00 Voltage Output fail
2025-07-12T05:30:09+03:00 System started
2025-07-12T05:30:09+03:00 Cable unlocked
2025-07-12T05:30:36+03:00 EV connected
2025-07-12T05:30:44+03:00 Start charging
2025-07-12T05:30:54+03:00 Voltage Input fail
2025-07-12T05:30:54+03:00 Voltage Output fail
2025-07-12T05:30:57+03:00 EVSE ready
2025-07-12T05:31:03+03:00 Start charging
2025-07-12T05:31:09+03:00 Voltage Input fail
2025-07-12T05:31:09+03:00 Voltage Output fail
2025-07-12T05:31:12+03:00 EVSE ready
2025-07-12T05:31:17+03:00 Start charging
2025-07-12T05:32:40+03:00 Charging done
2025-07-12T05:32:42+03:00 Start charging
2025-07-12T05:32:44+03:00 Voltage Input fail
2025-07-12T05:32:44+03:00 Voltage Output fail
2025-07-12T05:32:47+03:00 EVSE ready
2025-07-12T05:32:52+03:00 Start charging
2025-07-12T05:34:01+03:00 Charging done
2025-07-12T05:34:03+03:00 Start charging
2025-07-12T05:34:10+03:00 Voltage Input fail
2025-07-12T05:34:10+03:00 Voltage Output fail
2025-07-12T05:43:27+03:00 EV disconnected
2025-07-12T05:43:27+03:00 EVSE ready
2025-07-12T05:44:53+03:00 EV connected
2025-07-12T05:44:58+03:00 Start charging
2025-07-12T05:45:04+03:00 Voltage Input fail
2025-07-12T05:45:04+03:00 Voltage Output fail
2025-07-12T05:45:07+03:00 EVSE ready
2025-07-12T05:45:12+03:00 Start charging
2025-07-12T05:45:31+03:00 Voltage Input fail
2025-07-12T05:45:31+03:00 Voltage Output fail
2025-07-12T05:45:34+03:00 EVSE ready
2025-07-12T05:45:40+03:00 Start charging
2025-07-12T05:45:42+03:00 Voltage Input fail
2025-07-12T05:45:42+03:00 Voltage Output fail
2025-07-12T05:45:45+03:00 EVSE ready
2025-07-12T05:45:50+03:00 Start charging
2025-07-12T05:45:52+03:00 Voltage Input fail
2025-07-12T05:45:52+03:00 Voltage Output fail
2025-07-12T05:46:12+03:00 EV disconnected
2025-07-12T05:46:12+03:00 EVSE ready
2025-07-12T05:46:39+03:00 EV connected
2025-07-12T05:46:43+03:00 Start charging
2025-07-12T05:46:45+03:00 Voltage Output fail
2025-07-12T05:46:46+03:00 Voltage Input fail
2025-07-12T05:46:48+03:00 EVSE ready
2025-07-12T05:46:54+03:00 Start charging
2025-07-12T05:47:02+03:00 EV disconnected
2025-07-12T05:47:44+03:00 EV connected
2025-07-12T05:47:49+03:00 Start charging
2025-07-12T05:48:04+03:00 Voltage Input fail
2025-07-12T05:48:04+03:00 Voltage Output fail
2025-07-12T05:48:06+03:00 EVSE ready
2025-07-12T05:48:12+03:00 Start charging
2025-07-12T05:48:14+03:00 Voltage Input fail
2025-07-12T05:48:14+03:00 Voltage Output fail
2025-07-12T05:48:17+03:00 EVSE ready
2025-07-12T05:48:23+03:00 Start charging
2025-07-12T05:49:04+03:00 Charging done
2025-07-12T05:49:06+03:00 Start charging
2025-07-12T05:49:08+03:00 Voltage Input fail
2025-07-12T05:49:08+03:00 Voltage Output fail
2025-07-12T05:49:11+03:00 EVSE ready
2025-07-12T05:49:16+03:00 Start charging
2025-07-12T05:49:26+03:00 Voltage Input fail
2025-07-12T05:49:26+03:00 Voltage Output fail
2025-07-12T05:59:12+03:00 EVSE ready
2025-07-12T05:59:22+03:00 Start charging
2025-07-12T05:59:22+03:00 Cable locked
2025-07-12T05:59:24+03:00 Cable unlocked
2025-07-12T05:59:28+03:00 Voltage Input fail
2025-07-12T05:59:28+03:00 Voltage Output fail
2025-07-12T06:09:12+03:00 EVSE ready
2025-07-12T06:09:24+03:00 Start charging
2025-07-12T06:09:30+03:00 Voltage Input fail
2025-07-12T06:09:30+03:00 Voltage Output fail
2025-07-12T06:41:33+03:00 EV disconnected
2025-07-12T06:41:33+03:00 EVSE ready
2025-07-12T06:53:25+03:00 EV connected
2025-07-12T06:53:29+03:00 Start charging
2025-07-12T06:53:30+03:00 Charging done
2025-07-12T06:53:31+03:00 Start charging
2025-07-12T06:53:38+03:00 Voltage Input fail
2025-07-12T06:53:38+03:00 Voltage Output fail
2025-07-12T06:53:41+03:00 EVSE ready
2025-07-12T06:53:46+03:00 Start charging
2025-07-12T06:53:57+03:00 Voltage Input fail
2025-07-12T06:53:57+03:00 Voltage Output fail
2025-07-12T06:54:00+03:00 EVSE ready
2025-07-12T06:54:05+03:00 Start charging
2025-07-12T06:54:07+03:00 Voltage Input fail
2025-07-12T06:54:07+03:00 Voltage Output fail
2025-07-12T06:54:10+03:00 EVSE ready
2025-07-12T06:54:16+03:00 Start charging
2025-07-12T06:54:16+03:00 Cable locked
2025-07-12T06:54:17+03:00 Cable unlocked
2025-07-12T06:54:18+03:00 Voltage Input fail
2025-07-12T06:54:18+03:00 Voltage Output fail
2025-07-12T06:54:28+03:00 EV disconnected
2025-07-12T06:54:28+03:00 EVSE ready
2025-07-12T06:54:34+03:00 EV connected
2025-07-12T06:54:39+03:00 Start charging
2025-07-12T06:54:42+03:00 Voltage Input fail
2025-07-12T06:54:42+03:00 Voltage Output fail
2025-07-12T06:54:45+03:00 EVSE ready
2025-07-12T06:54:51+03:00 Start charging
2025-07-12T06:54:51+03:00 Cable locked
2025-07-12T06:54:52+03:00 Cable unlocked
2025-07-12T06:55:01+03:00 Voltage Input fail
2025-07-12T06:55:01+03:00 Voltage Output fail
2025-07-12T06:55:04+03:00 EVSE ready
2025-07-12T06:55:09+03:00 Start charging
2025-07-12T06:55:51+03:00 Charging done
2025-07-12T06:55:53+03:00 Start charging
2025-07-12T06:55:58+03:00 Voltage Input fail
2025-07-12T06:55:58+03:00 Voltage Output fail
2025-07-12T06:56:01+03:00 EVSE ready
2025-07-12T06:56:07+03:00 Start charging
2025-07-12T06:56:44+03:00 Charging done
2025-07-12T06:56:46+03:00 Start charging
2025-07-12T06:56:48+03:00 Voltage Input fail
2025-07-12T06:56:48+03:00 Voltage Output fail
2025-07-12T07:02:58+03:00 EV disconnected
2025-07-12T07:02:58+03:00 EVSE ready
2025-07-12T07:03:01+03:00 EV connected
2025-07-12T07:03:06+03:00 Start charging
2025-07-12T07:03:08+03:00 Voltage Input fail
2025-07-12T07:03:08+03:00 Voltage Output fail
2025-07-12T07:03:11+03:00 EVSE ready
2025-07-12T07:03:13+03:00 EV disconnected
2025-07-12T07:40:51+03:00 EV connected
2025-07-12T07:40:56+03:00 Start charging
2025-07-12T07:41:02+03:00 Voltage Input fail
2025-07-12T07:41:02+03:00 Voltage Output fail
2025-07-12T07:41:06+03:00 EVSE ready
2025-07-12T07:41:12+03:00 Start charging
2025-07-12T07:41:14+03:00 Voltage Input fail
2025-07-12T07:41:14+03:00 Voltage Output fail
2025-07-12T07:41:17+03:00 EVSE ready
2025-07-12T07:41:22+03:00 Start charging
2025-07-12T07:42:01+03:00 Charging done
2025-07-12T07:42:03+03:00 Start charging
2025-07-12T07:42:08+03:00 Voltage Input fail
2025-07-12T07:42:08+03:00 Voltage Output fail
2025-07-12T07:42:11+03:00 EVSE ready
2025-07-12T07:42:17+03:00 Start charging
2025-07-12T07:42:19+03:00 Voltage Input fail
2025-07-12T07:42:19+03:00 Voltage Output fail
2025-07-12T07:42:26+03:00 EV disconnected
2025-07-12T07:42:26+03:00 EVSE ready
2025-07-12T09:07:42+03:00 System started
2025-07-12T09:09:04+03:00 EV connected
2025-07-12T09:09:09+03:00 Start charging
2025-07-12T09:09:15+03:00 Voltage Input fail
2025-07-12T09:09:15+03:00 Voltage Output fail
2025-07-12T09:09:18+03:00 EVSE ready
2025-07-12T09:09:23+03:00 Start charging
2025-07-12T09:09:23+03:00 Cable locked
2025-07-12T09:09:25+03:00 Cable unlocked
2025-07-12T09:09:26+03:00 Voltage Output fail
2025-07-12T09:09:27+03:00 Voltage Input fail
2025-07-12T09:09:29+03:00 EVSE ready
2025-07-12T09:09:35+03:00 Start charging
2025-07-12T09:10:12+03:00 Charging done
2025-07-12T09:10:13+03:00 Start charging
2025-07-12T09:10:13+03:00 Cable locked
2025-07-12T09:10:14+03:00 Cable unlocked
2025-07-12T09:10:15+03:00 Voltage Output fail
2025-07-12T09:10:16+03:00 Voltage Input fail
2025-07-12T09:10:18+03:00 EVSE ready
2025-07-12T09:10:19+03:00 EV disconnected
2025-07-12T21:54:06+03:00 EV connected
2025-07-12T21:54:10+03:00 Start charging
2025-07-12T21:54:16+03:00 Voltage Input fail
2025-07-12T21:54:16+03:00 Voltage Output fail
2025-07-12T21:54:19+03:00 EVSE ready
2025-07-12T21:54:25+03:00 Start charging
2025-07-12T22:29:13+03:00 Charging done
2025-07-12T22:29:15+03:00 Start charging
2025-07-12T22:29:21+03:00 Voltage Input fail
2025-07-12T22:29:21+03:00 Voltage Output fail
2025-07-12T22:29:24+03:00 EVSE ready
2025-07-12T22:29:30+03:00 Start charging
2025-07-12T22:29:34+03:00 Voltage Input fail
2025-07-12T22:29:34+03:00 Voltage Output fail
2025-07-12T22:29:37+03:00 EVSE ready
2025-07-12T22:29:42+03:00 Start charging
2025-07-12T22:29:51+03:00 Voltage Input fail
2025-07-12T22:29:51+03:00 Voltage Output fail
2025-07-12T22:38:58+03:00 EVSE ready
2025-07-12T22:39:07+03:00 Start charging
2025-07-12T22:39:14+03:00 Voltage Input fail
2025-07-12T22:39:14+03:00 Voltage Output fail
2025-07-12T22:48:34+03:00 EV disconnected
2025-07-12T22:48:34+03:00 EVSE ready
2025-07-12T22:48:38+03:00 EV connected
2025-07-12T22:48:43+03:00 Start charging
2025-07-12T22:48:54+03:00 Voltage Input fail
2025-07-12T22:48:54+03:00 Voltage Output fail
2025-07-12T22:48:57+03:00 EVSE ready
2025-07-12T22:49:02+03:00 Start charging
2025-07-12T22:49:13+03:00 Voltage Input fail
2025-07-12T22:49:13+03:00 Voltage Output fail
2025-07-12T22:49:16+03:00 EVSE ready
2025-07-12T22:49:21+03:00 Start charging
2025-07-12T22:49:56+03:00 Charging done
2025-07-12T22:49:58+03:00 Start charging
2025-07-12T22:50:00+03:00 Voltage Input fail
2025-07-12T22:50:00+03:00 Voltage Output fail
2025-07-12T22:50:03+03:00 EVSE ready
2025-07-12T22:50:08+03:00 Start charging
2025-07-12T22:50:58+03:00 Charging done
2025-07-12T22:51:00+03:00 Start charging
2025-07-12T22:51:05+03:00 Voltage Input fail
2025-07-12T22:51:05+03:00 Voltage Output fail
2025-07-12T22:51:58+03:00 EV disconnected
2025-07-12T22:51:58+03:00 EVSE ready
2025-07-12T22:52:01+03:00 EV connected
2025-07-12T22:52:06+03:00 Start charging
2025-07-12T22:52:20+03:00 Voltage Input fail
2025-07-12T22:52:20+03:00 Voltage Output fail
2025-07-12T22:52:22+03:00 EVSE ready
2025-07-12T22:52:28+03:00 Start charging
2025-07-12T22:52:34+03:00 Voltage Input fail
2025-07-12T22:52:34+03:00 Voltage Output fail
2025-07-12T22:52:37+03:00 EVSE ready
2025-07-12T22:52:42+03:00 Start charging
2025-07-12T22:52:52+03:00 Voltage Input fail
2025-07-12T22:52:52+03:00 Voltage Output fail
2025-07-12T22:52:55+03:00 EVSE ready
2025-07-12T22:53:00+03:00 Start charging
2025-07-12T22:53:00+03:00 Cable locked
2025-07-12T22:53:01+03:00 Cable unlocked
2025-07-12T22:53:02+03:00 Voltage Input fail
2025-07-12T22:53:02+03:00 Voltage Output fail
2025-07-12T22:53:14+03:00 EV disconnected
2025-07-12T22:53:14+03:00 EVSE ready
2025-07-12T22:53:22+03:00 EV connected
2025-07-12T22:53:27+03:00 Start charging
2025-07-12T23:01:12+03:00 Charging done
2025-07-12T23:01:14+03:00 Start charging
2025-07-12T23:01:17+03:00 Voltage Input fail
2025-07-12T23:01:17+03:00 Voltage Output fail
2025-07-12T23:01:19+03:00 EVSE ready
2025-07-12T23:01:25+03:00 Start charging
2025-07-12T23:01:27+03:00 Voltage Input fail
2025-07-12T23:01:27+03:00 Voltage Output fail
2025-07-12T23:01:30+03:00 EVSE ready
2025-07-12T23:01:36+03:00 Start charging
2025-07-12T23:01:36+03:00 Cable locked
2025-07-12T23:01:37+03:00 Cable unlocked
2025-07-12T23:01:38+03:00 Voltage Input fail
2025-07-12T23:01:38+03:00 Voltage Output fail
2025-07-12T23:01:40+03:00 EVSE ready
2025-07-12T23:01:46+03:00 Start charging
2025-07-12T23:02:14+03:00 Voltage Input fail
2025-07-12T23:02:14+03:00 Voltage Output fail
2025-07-12T23:12:02+03:00 EVSE ready
2025-07-12T23:12:14+03:00 Start charging
2025-07-12T23:12:27+03:00 Voltage Input fail
2025-07-12T23:12:27+03:00 Voltage Output fail
2025-07-12T23:17:00+03:00 EV disconnected
2025-07-12T23:17:00+03:00 EVSE ready
2025-07-13T07:44:07+03:00 EV connected
2025-07-13T07:44:11+03:00 Start charging
2025-07-13T07:44:30+03:00 Voltage Input fail
2025-07-13T07:44:30+03:00 Voltage Output fail
2025-07-13T07:44:33+03:00 EVSE ready
2025-07-13T07:44:39+03:00 Start charging
2025-07-13T07:44:41+03:00 Voltage Input fail
2025-07-13T07:44:41+03:00 Voltage Output fail
2025-07-13T07:44:44+03:00 EVSE ready
2025-07-13T07:44:49+03:00 Start charging
2025-07-13T07:45:12+03:00 Voltage Input fail
2025-07-13T07:45:12+03:00 Voltage Output fail
2025-07-13T07:45:15+03:00 EVSE ready
2025-07-13T07:45:20+03:00 Start charging
2025-07-13T07:45:22+03:00 Voltage Input fail
2025-07-13T07:45:22+03:00 Voltage Output fail
2025-07-13T07:45:40+03:00 EV disconnected
2025-07-13T07:45:40+03:00 EVSE ready
2025-07-13T07:45:58+03:00 EV connected
2025-07-13T07:46:03+03:00 Start charging
2025-07-13T07:46:05+03:00 Voltage Input fail
2025-07-13T07:46:05+03:00 Voltage Output fail
2025-07-13T07:46:08+03:00 EVSE ready
2025-07-13T07:46:13+03:00 Start charging
2025-07-13T07:46:20+03:00 Voltage Input fail
2025-07-13T07:46:20+03:00 Voltage Output fail
2025-07-13T07:46:23+03:00 EVSE ready
2025-07-13T07:46:28+03:00 Start charging
2025-07-13T07:46:32+03:00 Charging done
2025-07-13T07:46:33+03:00 EV disconnected
2025-07-13T07:46:41+03:00 EV connected
2025-07-13T07:46:47+03:00 Start charging
2025-07-13T07:50:11+03:00 Charging done
2025-07-13T07:50:13+03:00 Start charging
2025-07-13T07:50:15+03:00 Voltage Input fail
2025-07-13T07:50:15+03:00 Voltage Output fail
2025-07-13T07:50:18+03:00 EVSE ready
2025-07-13T07:50:23+03:00 Start charging
2025-07-13T07:51:01+03:00 Charging done
2025-07-13T07:51:03+03:00 Start charging
2025-07-13T07:51:08+03:00 Voltage Input fail
2025-07-13T07:51:08+03:00 Voltage Output fail
2025-07-13T07:51:11+03:00 EVSE ready
2025-07-13T07:51:17+03:00 Start charging
2025-07-13T07:51:28+03:00 Voltage Input fail
2025-07-13T07:51:28+03:00 Voltage Output fail
2025-07-13T07:51:31+03:00 EVSE ready
2025-07-13T07:51:37+03:00 Start charging
2025-07-13T07:51:46+03:00 Voltage Input fail
2025-07-13T07:51:46+03:00 Voltage Output fail
2025-07-13T07:55:13+03:00 EV disconnected
2025-07-13T07:55:13+03:00 EVSE ready
2025-07-13T07:55:16+03:00 EV connected
2025-07-13T07:55:20+03:00 Start charging
2025-07-13T07:55:22+03:00 Voltage Output fail
2025-07-13T07:55:23+03:00 Voltage Input fail
2025-07-13T07:55:25+03:00 EVSE ready
2025-07-13T07:55:31+03:00 Start charging
2025-07-13T07:55:33+03:00 Voltage Input fail
2025-07-13T07:55:33+03:00 Voltage Output fail
2025-07-13T07:55:36+03:00 EVSE ready
2025-07-13T07:55:42+03:00 EV disconnected
2025-07-13T19:53:04+03:00 EV connected
2025-07-13T19:53:10+03:00 Start charging
2025-07-13T19:53:12+03:00 Voltage Input fail
2025-07-13T19:53:12+03:00 Voltage Output fail
2025-07-13T19:53:15+03:00 EVSE ready
2025-07-13T19:53:20+03:00 Start charging
2025-07-13T19:53:22+03:00 Voltage Output fail
2025-07-13T19:53:23+03:00 Voltage Input fail
2025-07-13T19:53:25+03:00 EVSE ready
2025-07-13T19:53:31+03:00 Start charging
2025-07-13T19:54:13+03:00 Charging done
2025-07-13T19:54:15+03:00 Start charging
2025-07-13T19:54:17+03:00 Voltage Input fail
2025-07-13T19:54:17+03:00 Voltage Output fail
2025-07-13T19:54:20+03:00 EVSE ready
2025-07-13T19:54:25+03:00 Start charging
2025-07-13T19:55:06+03:00 Charging done
2025-07-13T19:55:07+03:00 EV disconnected
2025-07-13T19:55:45+03:00 EV connected
2025-07-13T19:55:51+03:00 Start charging
2025-07-13T19:55:57+03:00 Voltage Input fail
2025-07-13T19:55:57+03:00 Voltage Output fail
2025-07-13T19:55:59+03:00 EVSE ready
2025-07-13T19:56:05+03:00 Start charging
2025-07-13T19:56:07+03:00 Voltage Input fail
2025-07-13T19:56:07+03:00 Voltage Output fail
2025-07-13T19:56:10+03:00 EVSE ready
2025-07-13T19:56:15+03:00 EV disconnected
2025-07-14T08:01:37+03:00 EV connected
2025-07-14T08:01:45+03:00 Start charging
2025-07-14T08:01:45+03:00 Cable locked
2025-07-14T08:01:46+03:00 Cable unlocked
2025-07-14T08:01:47+03:00 Voltage Output fail
2025-07-14T08:01:48+03:00 Voltage Input fail
2025-07-14T08:01:50+03:00 EVSE ready
2025-07-14T08:01:56+03:00 Start charging
2025-07-14T08:03:37+03:00 Charging done
2025-07-14T08:03:39+03:00 Start charging
2025-07-14T08:03:43+03:00 Voltage Input fail
2025-07-14T08:03:43+03:00 Voltage Output fail
2025-07-14T08:03:46+03:00 EVSE ready
2025-07-14T08:03:52+03:00 Start charging
2025-07-14T08:04:55+03:00 Charging done
2025-07-14T08:04:58+03:00 Start charging
2025-07-14T08:05:00+03:00 Voltage Input fail
2025-07-14T08:05:00+03:00 Voltage Output fail
2025-07-14T08:05:02+03:00 EVSE ready
2025-07-14T08:05:08+03:00 Start charging
2025-07-14T08:05:10+03:00 Voltage Input fail
2025-07-14T08:05:10+03:00 Voltage Output fail
2025-07-14T08:14:24+03:00 EVSE ready
2025-07-14T08:14:34+03:00 Start charging
2025-07-14T08:14:36+03:00 Voltage Output fail
2025-07-14T08:14:37+03:00 Voltage Input fail
2025-07-14T08:17:18+03:00 EV disconnected
2025-07-14T08:17:19+03:00 EVSE ready
2025-07-15T07:23:28+03:00 EV connected
2025-07-15T07:23:33+03:00 Start charging
2025-07-15T07:23:39+03:00 Voltage Input fail
2025-07-15T07:23:39+03:00 Voltage Output fail
2025-07-15T07:23:42+03:00 EVSE ready
2025-07-15T07:23:47+03:00 Start charging
2025-07-15T07:23:49+03:00 Voltage Output fail
2025-07-15T07:23:50+03:00 Voltage Input fail
2025-07-15T07:23:53+03:00 EVSE ready
2025-07-15T07:23:58+03:00 Start charging
2025-07-15T07:24:00+03:00 Voltage Input fail
2025-07-15T07:24:00+03:00 Voltage Output fail
2025-07-15T07:24:03+03:00 EVSE ready
2025-07-15T07:24:10+03:00 Start charging
2025-07-15T07:24:47+03:00 Charging done
2025-07-15T07:24:49+03:00 Start charging
2025-07-15T07:24:54+03:00 Voltage Input fail
2025-07-15T07:24:54+03:00 Voltage Output fail
2025-07-15T07:25:41+03:00 EV disconnected
2025-07-15T07:25:41+03:00 EVSE ready
2025-07-16T19:26:29+03:00 System started
2025-07-16T19:30:53+03:00 EV connected
2025-07-16T19:30:57+03:00 Start charging
2025-07-16T19:31:17+03:00 Voltage Input fail
2025-07-16T19:31:17+03:00 Voltage Output fail
2025-07-16T19:31:20+03:00 EVSE ready
2025-07-16T19:31:25+03:00 Start charging
2025-07-16T19:32:04+03:00 Charging done
2025-07-16T19:32:06+03:00 Start charging
2025-07-16T19:32:08+03:00 Voltage Input fail
2025-07-16T19:32:08+03:00 Voltage Output fail
2025-07-16T19:32:11+03:00 EVSE ready
2025-07-16T19:32:16+03:00 Start charging
2025-07-16T19:32:18+03:00 Voltage Input fail
2025-07-16T19:32:18+03:00 Voltage Output fail
2025-07-16T19:32:21+03:00 EVSE ready
2025-07-16T19:32:22+03:00 EV disconnected
2025-07-16T19:32:44+03:00 System started
-----END EVENT LOG-----
-----BEGIN TS LOG-----
2025-07-14T08:14:36+03:00 Charge data Output voltage fail:
Input Voltage L1 237 V
Input Voltage L2 240 V
Input Voltage L3 0 V
Input Voltage N 2 V
Output Voltage L1 236 V
Output Voltage L2 239 V
Output Voltage L3 0 V
Output Voltage N 2 V
Current L1 0.6 A
Current L2 0.6 A
Current L3 0.3 A
Current N 0.3 A
Current limit cause grid
CP duty cycle 0 %
Phase used None
Was charging True
2025-07-14T08:14:36+03:00 Charge data Input voltage fail:
Input Voltage L1 240 V
Input Voltage L2 239 V
Input Voltage L3 111 V
Input Voltage N 2 V
Output Voltage L1 138 V
Output Voltage L2 141 V
Output Voltage L3 0 V
Output Voltage N 2 V
Current L1 0.4 A
Current L2 0.4 A
Current L3 0.3 A
Current N 0.1 A
Current limit cause grid
CP duty cycle 0 %
Phase used None
Was charging True
2025-07-15T07:23:37+03:00 Charge data Charging:
Input Voltage L1 239 V
Input Voltage L2 234 V
Input Voltage L3 11 V
Input Voltage N 1 V
Output Voltage L1 237 V
Output Voltage L2 232 V
Output Voltage L3 11 V
Output Voltage N 1 V
Current L1 0.5 A
Current L2 0.5 A
Current L3 0.1 A
Current N 0.3 A
Current limit cause load balance
CP duty cycle 17 %
Phase used Three ph
Was charging True
2025-07-15T07:23:38+03:00 Charge data Input voltage fail:
Input Voltage L1 235 V
Input Voltage L2 236 V
Input Voltage L3 62 V
Input Voltage N 1 V
Output Voltage L1 212 V
Output Voltage L2 225 V
Output Voltage L3 2 V
Output Voltage N 1 V
Current L1 0.4 A
Current L2 0.5 A
Current L3 0.1 A
Current N 0.3 A
Current limit cause load balance
CP duty cycle 0 %
Phase used None
Was charging True
2025-07-15T07:23:38+03:00 Charge data Output voltage fail:
Input Voltage L1 235 V
Input Voltage L2 236 V
Input Voltage L3 62 V
Input Voltage N 1 V
Output Voltage L1 212 V
Output Voltage L2 225 V
Output Voltage L3 2 V
Output Voltage N 1 V
Current L1 0.4 A
Current L2 0.5 A
Current L3 0.1 A
Current N 0.3 A
Current limit cause load balance
CP duty cycle 0 %
Phase used None
Was charging True
2025-07-15T07:23:49+03:00 Charge data Output voltage fail:
Input Voltage L1 237 V
Input Voltage L2 238 V
Input Voltage L3 0 V
Input Voltage N 1 V
Output Voltage L1 235 V
Output Voltage L2 237 V
Output Voltage L3 0 V
Output Voltage N 1 V
Current L1 0.5 A
Current L2 0.5 A
Current L3 0.1 A
Current N 0.3 A
Current limit cause grid
CP duty cycle 17 %
Phase used Three ph
Was charging True
2025-07-16T19:31:29+03:00 Charge data Charging:
Input Voltage L1 238 V
Input Voltage L2 234 V
Input Voltage L3 235 V
Input Voltage N 0 V
Output Voltage L1 237 V
Output Voltage L2 0 V
Output Voltage L3 0 V
Output Voltage N 1 V
Current L1 0.6 A
Current L2 0.1 A
Current L3 0.2 A
Current N 0.6 A
Current limit cause grid
CP duty cycle 17 %
Phase used L1
Was charging True
2025-07-16T19:32:07+03:00 Charge data Output voltage fail:
Input Voltage L1 240 V
Input Voltage L2 232 V
Input Voltage L3 52 V
Input Voltage N 0 V
Output Voltage L1 219 V
Output Voltage L2 210 V
Output Voltage L3 0 V
Output Voltage N 0 V
Current L1 0.3 A
Current L2 0.4 A
Current L3 0.2 A
Current N 0.1 A
Current limit cause grid
CP duty cycle 0 %
Phase used None
Was charging True
2025-07-16T19:32:07+03:00 Charge data Input voltage fail:
Input Voltage L1 239 V
Input Voltage L2 232 V
Input Voltage L3 92 V
Input Voltage N 0 V
Output Voltage L1 131 V
Output Voltage L2 125 V
Output Voltage L3 0 V
Output Voltage N 0 V
Current L1 0.2 A
Current L2 0.2 A
Current L3 0.2 A
Current N 0.0 A
Current limit cause grid
CP duty cycle 0 %
Phase used None
Was charging True
2025-07-16T19:32:18+03:00 Charge data Output voltage fail:
Input Voltage L1 241 V
Input Voltage L2 233 V
Input Voltage L3 0 V
Input Voltage N 0 V
Output Voltage L1 239 V
Output Voltage L2 232 V
Output Voltage L3 0 V
Output Voltage N 0 V
Current L1 0.4 A
Current L2 0.4 A
Current L3 0.2 A
Current N 0.2 A
Current limit cause load balance
CP duty cycle 0 %
Phase used None
Was charging True
2025-07-16T19:32:18+03:00 Charge data Input voltage fail:
Input Voltage L1 239 V
Input Voltage L2 235 V
Input Voltage L3 99 V
Input Voltage N 0 V
Output Voltage L1 109 V
Output Voltage L2 106 V
Output Voltage L3 0 V
Output Voltage N 0 V
Current L1 0.2 A
Current L2 0.2 A
Current L3 0.2 A
Current N 0.0 A
Current limit cause load balance
CP duty cycle 0 %
Phase used None
Was charging True
2025-07-16T19:32:43+03:00 DLB data Not enough power:
Available grid amps L1 10.0 A
Available grid amps L2 10.0 A
Available grid amps L3 10.2 A
Available solar amps L1 0.0 A
Available solar amps L2 0.0 A
Available solar amps L3 0.2 A
Energy amps L1 0.0 A
Energy amps L2 0.0 A
Energy amps L3 0.0 A
-----END TS LOG-----
-----BEGIN TROUBLESHOOT-----
g+qx0ndowCcAtem30ndowScAx+630ndowgQDaQAFwMLTd2jDBCBpAAHA1tN3aMQEaCAAAcDW03doxQQBaQAGwNfTd2jGBCBpAAXA19N3aMcEImkACsDX03doyAgHae9hAArA19N3aMkICGntYQAKwNfTd2jKCAlpa2EACsDX03doywgKaWAgAArA19N3aMwIC2kFYQAKwNfTd2jNCAxpBWEACsDX03dozggNaWAgAArA19N3aM8IDmlgIAAKwNfTd2jQCIBp8GEACsDX03do0QiBae1hAArA19N3aNIIgmlsYQAKwNfTd2jTCINplwFCAArA19N3aNQIhGkyAUIACsDX03do1QiFaQwBQgAKwNfTd2jWCIZpBWEACsDX03do1wiHaQVhAArA19N3aNgIiGlgIAAKwNjTd2jZCIlpCWEACsDY03do2giKaQVhAArA2NN3aNsIi2kFYQALwNjTd2jcCCBp5mEAC8DY03do3QghaQphAAvA2NN3aN4IImkKYQACwNnTd2jfBGggAALA2dN3aOAEAWkABcDe03do4QQgaQAGwN7Td2jiBCJpAAbAItR3aOMEIGYABcAi1Hdo5AQxZgAGwAXUd2jlBDFpAAXAB9R3aOYEIGkAAcAK1Hdo5wRoIAABwArUd2joBAFpAAbACtR3aOkEIGkABcAK1Hdo6gQiaQAKwAvUd2jrCAdp7GEACsAL1Hdo7AgIaexhAArAC9R3aO0ICWl9YQAKwAvUd2juCAppYCAACsAL1Hdo7wgLaWAgAArAC9R3aPAIDGlgIAAKwAvUd2jxCA1pYCAACsAL1Hdo8ggOaQFhAArAC9R3aPMIgGnxYQAKwAvUd2j0CIFp6mEACsAL1Hdo9QiCaX1hAArADNR3aPYIg2mUAUIACsAM1Hdo9wiEaT4BQgAKwAzUd2j4CIVpCQFCAArADNR3aPkIhmlgIAAKwAzUd2j6CIdpYCAACsAM1Hdo+wiIaWAgAArADNR3aPwIiWlgIAAKwAzUd2j9CIppYCAACsAM1Hdo/giLaWAgAAvADNR3aP8IIGnmYQALwAzUd2gmCCFiCmEAC8AM1HdoAQgiaQphAALADdR3aAIEaCAAAsAN1HdoAwQBaQAFwBLUd2gEBCBpAAbAEtR3aAUEImkAAcAT1HdoBgRoIAABwBPUd2gHBAFpAAXAE9R3aAgEImkACsAT1HdoCQgHafFhAArAE9R3aAoICGnpYQAKwBTUd2gLCAlpYCAACsAU1HdoDAgKaWAgAArAFNR3aA0IC2nwYQAKwBTUd2gOCAxp6GEACsAU1HdoDwgNaWAgAArAFNR3aBAIDmlgIAAKwBTUd2gRCIBp8mEACsAU1HdoEgiBaephAArAFNR3aBMIgmkBYQAKwBTUd2gUCINpkwFCAArAFNR3aBUIhGnpYQAKwBXUd2gWCIVp8mEACsAV1HdoFwiGafBhAArAFdR3aBgIh2noYQAKwBXUd2gZCIhpYCAACsAV1HdoGgiJaZEBQgAKwBXUd2gbCIpp5mEACsAV1HdoHAiLafFhAAvAFdR3aB0IIGnmYQALwBXUd2geCCFpCmEAC8AV1HdoHwgiaQphAALAF9R3aCAEaCAAAsAX1HdoIQQBaQAGwBfUd2giBCBpAAbAF9R3aCMEImkAg+oo1HdowCcAtekt1HdowScAx+4t1HdowgQDaQAb6RkweWjDJwA=YvMZMHloxAkxqQgwGTChAOL1GTB5aMUKNjAwMzg0NzQ2M7IAuugZMHloxgMwMzSrAEfxGTB5aMcHdjEuMTQuN68ACcAZMHloyAgCaWAgAAnAGjB5aMkIA2kBYQAJwBoweWjKCAVpAWEACcAaMHloywgGaWAgAAnAGjB5aMwIB2lgIAAJwBoweWjNCAhpYCAACcAaMHlozggJaQFhAAnAGjB5aM8IC2lgIAAJwBoweWjQCA1pYCAACcAaMHlo0QgQaWAgAAnAGjB5aNIIEWkBYQAJwBoweWjTCBNpYCAACcAaMHlo1AgUaWAgAAnAGjB5aNUIGGkBYQAJwBoweWjWCBlpAWEACcAaMHlo1wgaaWAgAAnAGjB5aNgIHmlgIAAJwBoweWjZCCJpYCAACcAaMHlo2ggjaWAgAAnAGzB5aNsIKGlgIAAJwBsweWjcCClpAWEACcAbMHlo3Qg5aQFhAAnAGzB5aN4IOmlgIAAJwBsweWjfCDtpYCAACcAbMHlo4Ag8aWAgAAnAGzB5aOEIPWkBYQAJwBsweWjiCD5pAWEACcAbMHlo4wg/aWAgAAnAGzB5aOQIQmkBYQAJwBsweWjlCENpYCAACcAcMHlo5ghEaWAgAAnAHDB5aOcITWlgIAAJwBwweWjoCE5pYCAACsAcMHlo6QgBaWAgAArAHDB5aOoIAmkBYQAKwBwweWjrCANpCmEACsAcMHlo7AgEaRBhAArAHDB5aO0IBWlkYQAKwBwweWjuCAdp6WEACsAcMHlo7wgIaethAArAHDB5aPAICWnoYQAKwBwweWjxCAppYCAACsAcMHlo8ggLaWAgAArAHDB5aPMIDGlgIAAKwBwweWj0CA1pYCAACsAdMHlo9QgOaWAgAArAHTB5aPYID2lgIAAKwB0weWj3CBBpYCAACsAdMHlo+AgRaWAgAArAHTB5aPkIEmkBYQAKwB0weWj6CBNpeQFCAArAHTB5aPsIFGl7AUIACsAdMHlo/AgVaRYBQgAKwB0weWj9CBZpYCAACsAdMHlo/ggXaWAgAArAHjB5aP8IGGl3YQAKwB4weWgmCBliA2EACsAeMHloAQgaaYf/QgAKwB4weWgCCBtpBwFCAArAHjB5aAMIHGlJAUIACsAeMHloBAgdaXESQgAKwB4weWgFCB5pAWEACsAeMHloBggfaWAgAArAHjB5aAcIIGlgIAAKwB4weWgICCFpYCAACsAeMHloCQglaWAgAArAHjB5aAoIJmlgIAAKwB4weWgLCCdpB2EACsAeMHloDAguaWAgAArAHjB5aA0IL2kBYQAKwB4weWgOCDBpmixCAArAHjB5aA8IMWkGYQAKwB8weWgQCDJpPAFCAArAHzB5aBEIQWkfYQAKwB8weWgSCEtpYCAACsAfMHloEwhMaWAgAArAHzB5aBQITWlgIAAKwB8weWgVCE5pYCAACsAfMHloFghPaWAgAArAHzB5aBcIWWkRYQAKwB8weWgYCFppD2EACsAfMHloGQhbaRRhAArAHzB5aBoIXGlgIAAKwCAweWgbCF1pYCAACsAgMHloHAheaWAgAArAIDB5aB0IX2lgIAAKwCAweWgeCGBpYCAACsAgMHloHwhhaWAgAArAIDB5aCAIYmkVF0IACsAgMHloIQhjaWAgAArAIDB5aCIIZGlgIAAKwCAweWgjCGVpYCAACsAgMHloJAhmaWAgAArAITB5aCUIaGmy+kIACsAhMHloJghpaWAgAArAITB5aCcIamlgIAAKwCEweWgoCGtpYCAACsAhMHloKQhsaWAgAArAITB5aCoIbmlgIAAKwCEweWgrCG9pZQJCAArAITB5aCwIcGlEAkIACsAhMHloLQhxacwBQgAKwCEweWguCHJpzAFCAArAITB5aC8Ic2kBYQAKwCEweWgwCHRpDGEACsAhMHloMQh1aRdhAArAITB5aDIIdmlgIAAKwCEweWgzCHtpYCAACsAhMHloNAh8aWAgAArAITB5aDUIfWlgIAAKwCEweWg2CIBp7GEACsAiMHloNwiBaethAArAIjB5aDgIgmnmYQAKwCIweWg5CINplgFCAArAIjB5aDoIhGmPAUIACsAiMHloOwiFaZEBQgAKwCIweWg8CIZpYCAACsAiMHloPQiHaWAgAArAIjB5aD4IiGlgIAAKwCMweWg/CIlpYCAACsAjMHloQAiKaWAgAArAIzB5aEEIi2lgIAAKwCMweWhCCJRpYCAAC8AjMHloQwgCaWAgAAvAIzB5aEQIA2kKYQALwCMweWhFCARpYCAAC8AjMHloRggFaQphAAvAIzB5aEcIBmkKYQALwCMweWhICAdpAmEAC8AjMHloSQgIaRlhAAvAIzB5aEoICWkHYQALwCMweWhLCAppEWEAC8AjMHloTAgLaRFhAAvAIzB5aE0IDGkRYQALwCMweWhOCA1pF2EAC8AkMHloTwgOaWAgAAvAJDB5aFAID2kBYQALwCQweWhRCBBpYCAAC8AkMHloUggSaWAgAAvAJDB5aFMIE2nqYQALwCQweWhUCBRp6GEAC8AkMHloVQgVaehhAAvAJDB5aFYIFmnv/0IAC8AkMHloVwgXafH/QgALwCUweWhYCBhpBmEAC8AlMHloWQgZaQFhAAvAJTB5aFoIGmkCYQALwCUweWhbCBtpAmEAC8AlMHloXAgcaQFhAAvAJTB5aF0IHWkBYQALwCUweWheCB5pYCAAC8AlMHloXwgfaQFhAAvAJTB5aGAIIGnmYQALwCUweWhhCCFpCmEAC8AlMHloYggiaQphAAvAJTB5aGMII2kKYQALwCUweWhkCCRpRmEAC8AlMHloZQglaVVhAAvAJTB5aGYIJmkGYQALwCUweWhnCChpYCAAC8AlMHloaAgpaWAgAAvAJTB5aGkIKmlgIAALwCUweWhqCCtpYCAAC8AlMHloawg4aRRhAAvAJTB5aGwIOWlgIAALwCYweWhtCDppAWEAC8AmMHlobghMaTJhAAvAJjB5aG8ITWkFYQALwCYweWhwCE5pHmEAC8AmMHlocQhPaQZhAAvAJjB5aHIIUmnkgEIAC8AmMHlocwhTaWiAQgALwCYweWh0CFRpr4BCAAvAJjB5aHUIVWlXgEIAC8AmMHlodghWaUiAQgALwCYweWh3CFdp/X9CAAvAJjB5aHgIWGlYgEIAC8AmMHloeQhZaZiAQgALwCcweWh6CFppu3pCAAvAJzB5aHsIW2mlekIAC8AnMHlofAhcacR6QgALwCcweWh9CF9pEGEAC8AnMHlofghgaWAgAAvAJzB5aH8IYWkQYQALwCcweWiACGJpAWEAC8AnMHlogQhjaTFhAAvAJzB5aIIIZGlgIAALwCcweWiDCGVp5mEAC8AnMHlohAhmaQFhAAvAKDB5aIUIZ2lgIAALwCgweWiGCG5pYCAAC8AoMHlohwhvaWAgAAvAKDB5aIgIcGlgIAALwCgweWiJCHFpYCAAC8AoMHloighyaWAgAAvAKDB5aIsIc2lvYQALwCgweWiMCHRpOmEAC8AoMHlojQh1aSe1QgALwCgweWiOCHZpjyxCAAvAKDB5aI8Id2lgIAALwCgweWiQCJFpYCAA3ucoMHlokScA-----END TROUBLESHOOT-----
-----BEGIN APP INFO-----
{
“serial_number”: “6003847463”,
“product_code”: “EVC111000000”,
“model”: “TeltoCharge”,
“fw”: “v1.14.7”,
“hw_rev”: “000”,
“app_version”: “iOS 18.5”,
“mobile_device_model”: “iPhone 11 Pro Max”
}
-----END APP INFO-----

I see there is very low voltage on the phase 3, means probably that somewhere is bad contact for the phase?

Hi, you’re correct. The L3 phase has very low voltage + there shouldn’t be 0V on neutral too. Check all of the input connections leading up to the charger.

This topic was automatically closed after 60 days. New replies are no longer allowed.