TRB143 M-Bus: specify device address in hex

Hi there,

I want to use the TRB143 to communicate to a heat-meter via M-Bus.
How do i specify the address in the wanted hex string format?
What prefix or suffix do I need to add?

I get the following error, while entering the string:
Numbers from 0 to 250 or 16 symbols length hexstring are allowed.

Thanks a lot!

Hi,

Welcome to Teltonika Networks Crowd Support!

If you know the device ID of the meter (i.e. 12345678), it can be inserted in the configuration as 12345678FFFFFFFF. This is done to restrict its search space when doing a full scan of the Bus. For more information, kindly refer to this link.

Let me know if this cleared your doubts.

Regards,

Thanks a lot!
That works a expected!