TBR143 Mbus reading schedule
Is it possible to make the reading of mbus devices occur every 15 minutes so that the reading occurs exactly every 15 minutes and the timestamps would be like this → 00:00, 00:15, 00:30, 00:45 etc…
or every 5 minutes
00:05, 00:10, 00:15 etc…
I got the hourly reading to work when I added 24 separate timings but this isn’t very handy way to do same every 15 or 5 minutes.
To achieve this, we need to go to Services > Modbus > Modbus TCP Client, and click edit on your created TCP device.
Then in the “Frequency” tab, select “Schedule”
In the “Schedule requests” tab enter “*:15:00” then add a new line and enter “*:30:00”.
Do this two more times for “*:45:00” and “*:00:00”. This should make the request be sent every 15th minute of every hour of the day.
The “*” Symbol is a wildcard, which means ‘any hour’ in this case
If you’d like for it to be every 5th minute of every hour, the Schedule request would look like this “*:05:00”; “*:10:00”; “*:15:00” and so on.
Excellent, this works just how you say and just what i looking for.
Thank you very much!